Mar 30 2017

Hot Patches on Fire Barriers

Q: In regards to penetrations through fire separations: Our latest survey from Joint Commission identified that “Hot Patches” (a piece of 5/8 sheet rock placed over a hole and the fire caulked around sheet rock) are not an effective way to seal a penetration. We just built a 90,000 square foot addition where builders used “hot patches”. Our district Deputy Fire Marshal states this is an acceptable method (not in writing). Your thoughts?

A: My thoughts…? I think the Deputy Fire Marshal is incorrect. He may accept them on behalf of the Fire Marshal office, but a ‘patch’ over a hole in a fire-rated barrier is not consistent with the UL listing of the way the fire-rated barrier was required to be built. The Joint Commission surveyor is correct. To maintain the UL listing of the fire-rated barrier, you would have to remove the section of gypsum board that has the hole from stud-to-stud, and cut in a new solid piece of gypsum board (without the hole of course) and secure it with the proper amount of screws, tape and joint compound as called for in the UL listing.

Just another example where one AHJ approves something, does not mean it is acceptable for another. The Joint Commission is not under any obligation to accept what the fire marshal says, and vice-versa… It is within the rights of the Deputy Fire Marshall to accept a ‘patch’ over a hole, but that is only for his review and approval. No other AHJ has to accept the fire marshal’s opinion and in this case, I believe the Joint Commission surveyor was correct in his observation.