Fire Door Annual Test & Inspection

Q: I’d like some clarification concerning the new requirement for annual fire door inspections: NFPA 101 2012, Chapter 7.2.1.15 States “Where required by Chapters 11 through 43, the following door assemblies shall be inspected ….”. I haven’t found anything in Chapters 18 or 19 that specifically require the annual inspection. Additionally, the NFPA 101 Handbook specifically states that only occupancies requiring inspections are Assembly, Educational, Day-Care and Residential board and care. My question is where is the specific reference that is requiring hospitals to conduct annual fire door testing?

A: What you stated was actually section 7.2.1.15.1 which does not refer to fire-rated doors, but to certain doors in high-traffic areas, or doors of high importance, such as doors equipped with panic hardware, doors in exit enclosures, electrically controlled doors, or doors with special locking arrangements. Now some of these doors may be fire-rated, but section 7.2.1.15.1 does not specifically refer to fire-rated doors. Therefore, that is why this section is only required if the occupancy chapter requires it and you’re correct in saying the healthcare occupancies do not require it.

And you’re correct: These doors are only required to be tested in occupancies where the occupancy chapter specifically requires it. The healthcare occupancy chapters and the ambulatory healthcare occupancy chapters and the business occupancy chapters do NOT require it, so the test and inspection identified in 7.2.1.15.1 are not required in healthcare, ambulatory healthcare, and business occupancies. Now, if you have mixed occupancies in your hospital and have areas that could qualify as assembly occupancy (i.e. dining areas, auditoriums, large conference rooms, etc.) then you would have to make sure the doors identified in 7.2.1.15.1 are tested and inspected in those areas.

But look at section 19.1.1.4.1.1 which refers to fire-rated doors and at the end of this section, it says “See also Section 8.3.3.1”. Section 8.3.3.1 requires openings that are required to have a fire-protective rating (i.e. fire-rated doors) shall be protected, by approved, listed labeled fire door assemblies with the requirements of NFPA 80. Since NFPA 80 requires annual test and inspections of all fire doors, this is the section (not 7.2.1.15.2) that requires you to test and inspect your fire-rated doors.

The CMS S&C memo 17-38 which was issued on July 28, 2017, describes this issue as well. CMS re-adjusted their expected completion date for the first fire-door test and inspection from July 6, 2017 to January 1, 2018, but not all of the Accreditation Organizations followed suit. Check with your authorities having jurisdiction to confirm what date they are expecting you to complete your first fire-door test and inspection.

AHJ on Fire Door Inspections

Q:  Does the authority having jurisdiction have the final say whether or not an individual has the ‘knowledge and understanding’ required to perform fire door inspections?

A: Yes they do. Take a look at 4.6.1.1 of the 2012 LSC “The authority having jurisdiction shall determine whether the provisions of this Code are met.” That means the AHJ decides if the organization is compliant with the applicable NFPA codes and standards. But, keep in mind the typical hospital has 5 or 6 different AHJs that inspect their facility for compliance with the LSC:

  • CMS
  • Accreditation organization
  • State health department
  • State agency with over-sight on hospital construction
  • State fire marshal
  • Local fire inspector
  • Liability insurance company

Not one AHJ can over-ride another AHJ’s decision. All AHJs are equal… but different. If 5 AHJs say the qualifications of the person performing the fire door inspections are fine, but 1 AHJ says no, then the hospital must comply with the most restrictive requirements and comply with the latter AHJ’s desires. An AHJ may have rules and requirements that exceed NFPA standards, as well they should. NFPA standards are minimal standards, and most hospitals exceed the NFPA standards in some capacity, often due to local ordinances or state regulations (and sometimes at the whim of the design professional). But, if the AHJ decides to have standards that exceed the minimal NFPA requirements, they need to be able to justify that decision.

It is not at all uncommon for a healthcare organization to seek permission from a state or local AHJ (i.e. state fire marshal) to install a particular device or have a particular feature, only to find out later that their accreditation organization does not agree, and cites the issue. Both the state or local AHJ and the accreditation organization are correct; they are interpreting the Life Safety Code as they see fit. Whatever was approved by the state or local AHJ is just an approval for the state or local regulations. What was cited by the accreditation organization was cited based on the accreditation organization’s regulations and understanding of the Life Safety Code.

This is why healthcare organizations need to obtain permission and interpretations from all of their AHJs… not just one or two.

Fire Rated Doors in Non-Fire-Rated Walls

Q: If a fire door is in a wall that is not a fire-rated wall, will the wall need to be brought to be a fire-rated wall?

A: No… not typically. The location of fire-rated barriers (i.e. walls) are determined by the design professional (i.e. architect) when the facility is designed and constructed. Often times, after the facility is built and operating for a few years, new locations that require fire rated barriers are identified. These could include rooms that are newly designated as hazardous areas, or perhaps a building separation from a new addition.

It is not uncommon for some design professionals to specify fire-rated door assemblies in barriers that are not fire-rated. This may be due to a building code requirement, or it may be due to a misunderstanding of the codes and standards. For whatever reason, once these fire-rated door assemblies are installed, you must maintain them in accordance with NFPA 80 which includes annual fire-door testing and inspections. But there is no requirement to designate a barrier to be labeled as a fire-rated barrier simply because it has a fire-rated door assembly installed in it. To be sure where the fire-rated barriers are actually located, refer to the Life Safety drawings and/or original construction documents of the facility.

Fire Door Inspection Qualifications

Q: In regards to fire door inspections, what are the qualifications of the person to perform the inspection?

A: NFPA 80-2010, section 5.2.3.1 says fire doors must be tested by individuals with knowledge and understating of the operating components of the door assembly, but NFPA 80 does not identify or describe what ‘knowledge and understanding’ actually means. The word ‘qualified’ is not found in this context of describing the individual who performs this inspection. When the codes or standards are vague (as they often are), then it is up to the authorities having jurisdiction to decide how to interpret the code or standard (see 4.6.1.1 of the 2012 LSC). When the AHJ does not make an interpretation of the code or standard, then it is up to the individual facility to decide what’s right.

In this case, no national AHJ has published an interpretation for hospitals on what ‘knowledge and understanding’ is required to test and inspect fire door assemblies. Therefore, hospitals and other healthcare organizations have the right to decide what that means. However, during a survey or an inspection, the AHJ surveyor has the right to question how the hospital determined their individual has the ‘knowledge and understanding’ and if it is not satisfactory to the AHJ surveyor, then a citing may be in order.

My advice to healthcare organizations on this issue is to document why they believe their individual has the ‘knowledge and understanding’ to perform the inspections. If their maintenance person has worked on fire doors for 20 years then that may be sufficient evidence.

I also recommend healthcare organizations to sign their people up for an online course on fire door inspections, by using the link and coupon code located at the right-hand side of this web-page, to the International Fire Door Inspector Association (IFDIA).

Door Undercuts

Q: What is the maximum you can have between the bottom of door and the thresholds for a fire-rated door assembly? I have some stairwell doors with 1 inch to 1 ¼ inch gap between the bottom of the door and the threshold.

A: That will be a problem. According to section 8.3.3.1 of the 2012 Life Safety Code, you must install fire-rated door assemblies in accordance with NFPA 80-2010. Section 4.8.4.1 of NFPA 80-2010 says the clearance under the bottom of the door shall be a maximum of ¾ inch. Also, section 7.2.1.15.2 of the 2012 Life Safety Code says you must maintain the fire rated door assemblies in accordance with NFPA 80.

Any clearance under the bottom of the door (while it is in the closed position) that exceeds ¾ inch will be considered non-compliant. There are after-market devices available that you can install on the door to fill that gap, but you must be very careful as you can only install devices that have been listed by an independent testing laboratory (i.e. UL, FM Approval, Intertek) that have been approved for that purpose.

Keep in mind that there are limitations on the door material, amount of clearance, and the rating.  Here are links to information on 3 products suggested to me by Lori Greene (see her website at www.idighardware.com), but there may be more:

Zero:  http://idighardware.com/2013/03/solution-for-oversized-undercuts/

NGP:  http://idighardware.com/2015/01/new-products-for-oversized-fire-door-clearances/

Crown:  http://idighardware.com/2014/06/a-fire-door-test-first-hand/

Doors Wedged Open

Q: It has been our practice to not allow door hold open wedges on any door within the hospital. As far as code requirements go is it rated doors only, or does it include any door with a closer?

A: It applies to any fire rated door assembly, any non-rated door assembly that is required to be self-closing, and all corridor doors regardless of their fire-rating and regardless if they are self-closing.

Look at section 19.3.6.3.10 of the 2012 LSC, which says doors shall not be held open by devices other than those that release when the door is pushed or pulled. This section is part of section 19.3.6.3 “Corridor Doors” so it is referring to corridor doors only. Approved ‘push or pull’ release devices to hold a door open are the friction-fit type hold open that are integral to the door closer, and magnets. The logic here is a person could quickly push or pull the door closed, but if the door was wedged open, then the closing of the door would be slower and more difficult; therefore, wedging a door open would not be permitted.

Section 19.3.7.8 (1) of the 2012 LSC says doors in smoke barriers must be self-closing. The term ‘self-closing’ means the door has to close by itself without assistance. A smoke barrier door that is wedged open will not close by itself. Section 3.3.238 of the 2012 LSC defines “Self-closing” as a door equipped with an approved device that ensures closing after opening. All doors in hazardous areas are required to be self-closing regardless if the door is fire-rated or just smoke resistant.

To further make the point, section 19.2.2.2.7 of the 2012 LSC says any door in an exit passageway, stairway enclosure, horizontal exit, smoke barrier, or hazardous area enclosure shall be permitted to be held open only by automatic release device that complies with 7.2.1.8.2. The implication here is these doors must be self-closing and may only be held open by a device that releases the door (and allows the door to self-close) upon activation of the fire alarm system or sprinkler system.

And to finally address fire-rated door assemblies, section 8.3.3.1 requires all doors required to have a fire protection rating to comply with NFPA 80, which requires self-closing devices on the doors. So, any fire-rated door assembly may not be wedged open.

That applies to nearly all doors in a hospital. But there are some doors that you could actually wedge open, although you probably would not want to inform your staff. Doors located inside a suite of rooms that do not serve an exit or a hazardous area would be permitted to be wedged open because those rooms inside a suite are not required to have doors. But that’s about it.

Annual Test on Fire Rated Door Assemblies

Q: In regards to the new annual fire rated door assembly inspection, are we to inspect every door that has a fire rating or the doors that are located in fire-rated walls? I have noticed that not all fire doors in the building are located in fire rated walls, according to my Life Safety drawings. What do you say?

A: It is not uncommon for fire-rated door assemblies to be found in walls and barriers that are not fire-rated. This is often due to conflicting building codes that require 20-minute fire rated doors in all corridors, or a misunderstanding by the design professional. But make no mistake: You are required to test and inspect those doors on an annual basis.

My interpretation is based on section 7.2.1.15.2 of the 2012 LSC which says: “Fire-rated door assemblies shall be inspected and tested in accordance with NFPA 80…” This section of the LSC does not have any exceptions for fire-rated door assemblies that are located in walls and barriers that are not fire-rated.

Therefore, all fire-rated door assemblies must be inspected and tested in accordance with NFPA 80 on an annual basis, regardless where they are located.

Another way of looking at this issue is to review section 4.6.12.3 of the 2012 LSC which says existing life safety features that are obvious to the public, if not required by the LSC, must be either maintained or removed. The interpretation of what’s ‘obvious to the public’ is certainly open for discussion, but most fire-rated door assemblies can be determined by looking at a fire rating label on the hinge-side edge of the door, and that is viewable by the public. Whether it is obvious or not is a matter of opinion, but if you take the hardline on that, then all fire-rated doors (with a fire rating label) have to be maintained even if they are not located in a fire-rated barrier.

Either way… I think the LSC is pretty clear… you need to test and inspect all fire rated door assemblies regardless if they are located in a fire rated barrier. And by the way, the first test of the side-hinged swinging fire doors is due in a couple weeks: July 5, 2017. Better have it completed by then.

Poly Vinyl Mural on Fire Doors and Walls

Q: Is it permissible to completely cover a fire rated door in a hospital with a polyvinyl picture/mural? Also, is it permissible to cover a fire rated wall, from floor to ceiling in hospital with the same product?

A: No. You are not permitted to cover a fire-rated door with anything. Period. The reason why is, whatever is placed on the door will likely change the fire-resistive characteristics of the door and may likely allow the door to not last as long as it is designed.

Assuming the mural is newly installed, a poly-vinyl picture mural on the walls of the hospital may be permitted if it meets the requirements for interior finish. Class A interior finish is permitted on walls, and Class B is permitted in rooms where the capacity does not exceed four persons. A Class A material has a flame spread rating of 0 -25, and a Class B materials has a flame spread rating of 26 – 75.

Ask your supplier/vendor to provide the interior finish classification or the flame spread ratings to determine if you are compliant.

Fire Door Smoke Detectors

Q: I have a life safety consultant doing our annual inspection, and he keeps saying that I need to have individual smoke detectors for my corridor fire rated doors. The corridors on both sides of these doors are completely protected with smoke detectors, but he says regardless, that area smoke detectors are required next to the doors. Is this correct?

A: No, I don’t believe what the consultant is telling you is correct. Section 17.7.5.6.1 of NFPA 72 (2010) allows for either area smoke detectors or complete corridor smoke detector protection to activate the release of a hold-open on a door serving a fire barrier or a smoke compartment barrier. So, in regards to the cross-corridor doors that are held open by magnets connected to the fire alarm system, you are permitted to have one of the following:

  • A smoke detector on either side of the door mounted within five feet of the door; or smoke detectors mounted on both sides of the door within five feet if the transom above the door is greater than 24 inches.
  • The entire corridor where the cross-corridor door is located is properly protected with smoke detectors. A smoke detector must then be located within 15 feet of the door. For mounting locations for an area protected with detectors, the detectors must be no more than 15 feet from the wall (this is based on one-half of the maximum spacing distance between detectors which is 30 feet). The cross-corridor doors must be considered ‘closed’ when designing the detector locations, so that constitutes a “wall” and a detector is required within 15 feet of that wall.

Where consultants and surveyors have problems is they see a cross-corridor door held open by a magnet, and then they do not see a detector within five feet, and they believe that is a violation of NFPA 72. What they don’t consider is the corridor is completely protected with smoke detectors and NFPA 72 (2010) 17.6.3.1.1. (1) allows a detector to be one-half of the maximum spacing.

Fire Rated Door Assemblies

Q: I recently attended a conference where the speaker in the Life Safety session talked about the fire rating of the doors. She spoke of having the fire information labels on the doors. When I returned to the hospital, I found I only have about half the doors in my facility with the fire-rating labels. What do I need to do about this? Do I assume that all the doors are rated the same?

A: Fire-rated doors assemblies are required to have labels on the doors and on the door frames identifying that they are indeed fire-rated. The labels can be located on the side of the door or on the top of the door. Non-fire-rated door assemblies are not required to have any labels since there is no requirement for them to be fire-rated. In your case, it is reasonable to assume that not all door assemblies in your facility are actually required to be fire-rated and therefore do not have labels. You need to refer to your Life Safety drawings (or your original construction documents if your LS drawings are not accurate) to determine the location of the fire-rated doors assemblies in your facility, and then examine those door assemblies for compliance with the labeling requirements.

As a side note, I’ve been told by Mr. Jerry Rice, VP of DH Pace Company, Inc., that there is one exception to having labels on both the door and the frame. This would be on a ‘fire door assembly’ that comes from the factory as a complete assembly. These types of fire doors only have one label (none on the frame), and it is located under the top cap. The only sticker on the door is on the top cap that reads something like “Fire label under cap – Remove to view”. So, you would need to get on a ladder and take the cap off with a screwdriver if you want to see the label. Some AHJs deem that process is ‘not readily visible’ and push back, but most know of the door manufacturing process and accept the practice.

I personally have not seen these types of door assemblies in hospitals, but you need to be aware that they may be part of your facility.