Anteroom Door Closer

Category: Anteroom,Doors,Questions and AnswersBKeyes @ 12:00 am
Share

Q: We have an isolation room next to a nurse station in the Emergency room. The corridor door to the Anteroom has a door closer on it. My question: does the closer have to be on the anteroom door? I know that it has to be on the Isolation room door.

A: According to the Guidelines for Design and Construction of Health Care Facilities by the Facility Guidelines Institute (FGI), 2010 edition, if you have an anteroom (whether or not the anteroom is required) then the door to the anteroom must have a self-closing device. The FGI does say that anterooms are not required for airborne infection isolation (AII) rooms, but they are required for protective environment (PE) room, or a combination PE/AII room. If your organization has a PE room for emergency room patients, then it would require an anteroom, which in turn would require a closer on the door. The Life Safety Code would not require a closer on the anteroom door; however, the FGI would take precedent over the LSC in this matter.