AEM Program for Fire Alarm and Sprinklers

Category: AEM Program,Fire Alarm,Questions and Answers,SprinklersBKeyes @ 12:00 am
Share

Q: Are sprinklers, smoke detectors, etc. considered to be operating components of the utility systems? If so, our inspections are based on the pertinent NFPA references. I think that the fire system inspections could be considered preventive maintenance or at least the means to determine what maintenance needs to be completed. Can we use the CMS AEM program to alter our PM activities on the fire alarm and sprinkler systems?

A: You cannot use the CMS AEM program for Fire Alarm inspection and testing requirements. The CMS S&C letter 14-07 that describes the AEM program says the following regarding when the AEM program is not appropriate: “Other CoPs require adherence to manufacturer’s recommendations and/or set specific standards. For example: The National Fire Protection Association Life Safety Code (LSC) requirements incorporated by reference at 42 CFR 482.41(b) has some provisions that are pertinent to equipment maintenance, and compliance with these requirements are assessed on Federal surveys.”

So… you must follow the NFPA requirements specified for sprinkler and fire alarm testing and inspection, and the AEM program is not applicable.